I am performing a four bolt end plate moment connection design per AISC Design Guide 4. The design guide uses yield line theory to size the plate and column flange thickness. Reading through the text at the beginning, the design method tries to eliminate prying action by sizing the plate and column flange thick enough so that the stress does not exceed 90 percent of its capacity. The method calculates a “no prying moment” based off the strength of the connecting bolts. This “no prying moment” is then utilized to size the plate and the column flange.
I am having some issues with the design. The first step in the design examples is to calculate a required bolt diameter. In my case, the required bolt diameter is 0.545”. It is standard practice not to use anything less than a 3/4” diameter bolt, so that is what I would like to use. If I follow the design example, I would then use the strength of the 3/4” diameter bolt to calculate the “no prying moment” and then size my plate and column flange accordingly.
I have a hard time seeing why we should use the actual bolt diameter to calculate the “no prying moment” instead of using the required bolt diameter. By using the actual bolt diameter, the need for stiffeners is determined by the bolt size used instead of by the actual load. If I use 3/4" diameter bolts in my example, my column flange cannot handle the load and stiffeners would be required. A 5/8” diameter bolt would be adequate to handle the load. If I use 5/8” diameter bolts, my column flange is adequate and no stiffeners are required. This solution does not seem practical to me. Why should I have to use stiffeners just because I use a larger bolt diameter. Am I missing something? Does anyone else see an issue with using the required bolt diameter to calculate the “no prying moment” instead of the actual bolt diameter? If I do so using the same equations, I am still ensuring that the plate stress will not exceed 90 percent of its capacity, which follows the theory on which the whole design is based.
I am having some issues with the design. The first step in the design examples is to calculate a required bolt diameter. In my case, the required bolt diameter is 0.545”. It is standard practice not to use anything less than a 3/4” diameter bolt, so that is what I would like to use. If I follow the design example, I would then use the strength of the 3/4” diameter bolt to calculate the “no prying moment” and then size my plate and column flange accordingly.
I have a hard time seeing why we should use the actual bolt diameter to calculate the “no prying moment” instead of using the required bolt diameter. By using the actual bolt diameter, the need for stiffeners is determined by the bolt size used instead of by the actual load. If I use 3/4" diameter bolts in my example, my column flange cannot handle the load and stiffeners would be required. A 5/8” diameter bolt would be adequate to handle the load. If I use 5/8” diameter bolts, my column flange is adequate and no stiffeners are required. This solution does not seem practical to me. Why should I have to use stiffeners just because I use a larger bolt diameter. Am I missing something? Does anyone else see an issue with using the required bolt diameter to calculate the “no prying moment” instead of the actual bolt diameter? If I do so using the same equations, I am still ensuring that the plate stress will not exceed 90 percent of its capacity, which follows the theory on which the whole design is based.