Dec 20, 2002 #1 tyboy Electrical Joined Dec 20, 2002 Messages 8 Location US I cant remember the formula to determine phase to ground voltages in three phase systems, for example a 3 ph. 4160 system.
I cant remember the formula to determine phase to ground voltages in three phase systems, for example a 3 ph. 4160 system.
Dec 20, 2002 1 #2 twosockets Electrical Joined Dec 3, 2002 Messages 40 Location US tyboy, Assuming that it is a wye system that has 4160 volts phase to phase, the phase to grounded neutral voltage would be 2400 volts. You get that by taking the 4160 and dividing by the square root of 3 to obtain 2400. Upvote 0 Downvote
tyboy, Assuming that it is a wye system that has 4160 volts phase to phase, the phase to grounded neutral voltage would be 2400 volts. You get that by taking the 4160 and dividing by the square root of 3 to obtain 2400.