Hi, everyone. I am, once again, looking at an existing building's capacity for a ballasted PV system, which wil add approximately 4 psf dead load.
I have been through ASCE 7-05 calculations using several variables for the existing roof, but keep coming to the conclusion that the roof structure can't support it's own weight PRIOR to placement of a ballasted PV system.
This building utilizes a series of OWSJs supported by wide-flange beams and columns.
The roof itself consists of 20 ga. decking, lightweight concrete, and EPDM.
The roofer has lost his records (built in 1997) and I can't get a good idea of concrete deck thickness. The plans I have do not specify.
The joist I am analyzing is a 30K10, 6' OC, 43' span.
Here are my assumptions (dead load):
1. Sprinklers/lights: 5 psf
2. Ductwork: 4 psf
3. Suspended ceiling: 2 psf
4. Metal decking: 2.5 psf
5. EPDM roofing: 1 psf
6. Joist self weight: 2.5 psf
The lightweight concrete deck is specified as 3500 psi/115 pcf. I have been assuming that it is 2" thick at drains, increasing in thickness at 1/4" per ft. to the halfway point to the next drain, or approx. 22 ft (drains are 44' apart) This would give a concrete thickness of 7.5" at the thickest. This thick portion runs on/parallel to an entire joist in some locations. With the slope considered over the tributary area of the joist, this averages 7.125" of lightweight concrete concrete supported by one joist.
At this thickness, I am looking at 68.3 psf dead load from the concrete alone. Total dead load in this case (using numbers above) is 85.3 psf. The joist capacity (ASD) is 65.6 psf (43' span, 6' oc spacing).
This exceeds the allowable without snow load, drifting, wind, and live loads considered.
What the hell am I doing wrong?? I have read over and over that MINIMUM lt. wt. concrete roof deck thickness is typically 2", and minimum slope is .25"/ft. These are the assumptions I made. Does anyone know anything different?
The roofer did say that there was no polystyrene utilized under the concrete.
Any help in sorting this out would be greatly appreciated!!!
I have been through ASCE 7-05 calculations using several variables for the existing roof, but keep coming to the conclusion that the roof structure can't support it's own weight PRIOR to placement of a ballasted PV system.
This building utilizes a series of OWSJs supported by wide-flange beams and columns.
The roof itself consists of 20 ga. decking, lightweight concrete, and EPDM.
The roofer has lost his records (built in 1997) and I can't get a good idea of concrete deck thickness. The plans I have do not specify.
The joist I am analyzing is a 30K10, 6' OC, 43' span.
Here are my assumptions (dead load):
1. Sprinklers/lights: 5 psf
2. Ductwork: 4 psf
3. Suspended ceiling: 2 psf
4. Metal decking: 2.5 psf
5. EPDM roofing: 1 psf
6. Joist self weight: 2.5 psf
The lightweight concrete deck is specified as 3500 psi/115 pcf. I have been assuming that it is 2" thick at drains, increasing in thickness at 1/4" per ft. to the halfway point to the next drain, or approx. 22 ft (drains are 44' apart) This would give a concrete thickness of 7.5" at the thickest. This thick portion runs on/parallel to an entire joist in some locations. With the slope considered over the tributary area of the joist, this averages 7.125" of lightweight concrete concrete supported by one joist.
At this thickness, I am looking at 68.3 psf dead load from the concrete alone. Total dead load in this case (using numbers above) is 85.3 psf. The joist capacity (ASD) is 65.6 psf (43' span, 6' oc spacing).
This exceeds the allowable without snow load, drifting, wind, and live loads considered.
What the hell am I doing wrong?? I have read over and over that MINIMUM lt. wt. concrete roof deck thickness is typically 2", and minimum slope is .25"/ft. These are the assumptions I made. Does anyone know anything different?
The roofer did say that there was no polystyrene utilized under the concrete.
Any help in sorting this out would be greatly appreciated!!!