How much percentage of the ceiling is perforated? With high percentage penetration you will have problems with air stratification(not thermal, I mean). For example, with Laminar Air Flow Workstations,(i.e 100% face area) I found the drop in velocity at 30fpm per one foot. My idea is to keep atleast 50 fpm face velocity.
You also need to carefully design your duct work to avoid short circuiting of the air. I will prefer static regain method in this case.
Regards,