TAFEDout
Electrical
- Jul 28, 2007
- 6
With regard to calculating load sharing when paralleling transformers, and calculating short-circuit fault currents, how similar is Percentage Voltage Regulation (given with respect to full-load voltage) to Percentage Impedance?
I know how both quantities can be found by experiment/calculation; however, it would seem that for some (if not all) practical purposes the two quantity values might be interchangeable.
I assume that due to the much lower voltage during the short-circuit test to find/confirm the %Z, the Fe losses are negligible and therefore are not included when calculating %Z. Are there any other differences between Percentage Voltage Regulation and Percentage Impedance?
(Hopefully, I haven’t lost the plot - as all my reference texts apparently keep the two quantities very separate)