PCV vs UG-126(b)

Status
Not open for further replies.

torsani

Mechanical
Sep 4, 2001
25
Hi,

Does a globe valve with a pneumatic actuator (like a PCV), controlled by a self-actuated pilot valve (upstream signal) and fail position open meets with requirements of UG-126(b)?

Best regards

Torsani
 
Replies continue below

Recommended for you

UG-126(b) refers to pilot actuated relief valve, not a pressure control valve. PCV, as per my knowledge, cannot replace relief valve under any circumstances.

Untitled_urztdz.png




Dejan IVANOVIC
Process Engineer, MSChE
 
Pilot valves must be self-actuated. That is, they must be actuated by the pressure in the system and not by external sources such as electrical or pneumatics signals.

Therefore, the valve you describe does not meet UG126b.
 