PCA Circular tank Design

aalmasri

Structural
Jun 12, 2025
3
Hello All
I was going through the PCA circular tank design, and I noticed it calculates the ring steel by dividing by 0.9fy, while in some other places, it states that the steel stress should not exceed a specific value fs (20ksi for grade 60 steel and 14ksi for grade 40 steel). does anybody know a reason for this confusion?

in the old version of this document, As was T/fs, but in the newer version it is T/0.9fy. Am I right or what?

Thanks

1749760559588.png
1749760507156.png


1749760180160.png
 
Replies continue below

Recommended for you

The older one appears to be ASD while the newer is LRFD.

Old: Service level loads with allowable stresses.
New: Factored loads with nominal capacities (phi x max. strength)
 
Thanks JAE
After checking, both documents used factored load...
 
Well I would question that. The first of the two examples you posted uses the term "allowable" which is never used with factored loads.

Allowable.JPG
 
You were right, the old document used service loads, while the newer document used the factored load.
What confused me is ACI350, where in chapter 9 it discusses the load combinations and load factor, and then limits the stress to fs. I dont know if I should go with fs, or 0.9fy?