Partially Restrained Moment Connection
Hadeer Salah
EG
I need to design moment connection (beam to column flange) with 2 angles that shown on the attached file but i didn't find any approach to be followed.
Is there any solved example could help me?
Hadeer
 https://files.engineering.com/getfile.aspx?folder=67b60027-e507-4417-a216-926da4ed1b29&file=Cleat_Angle_moment_connection.PNG
I think that's considered a "Flexible Wind Connection". Or, pretty close to it.
I've never used them myself. But, the AISC LRFD 2nd edition volume II had a design procedure for it. Some caveats:
a) You're supposed to have a simple shear connection as well, like a shear tab or such.
b) You can't mix and match this with other moment connections.
c) Beams must be capable of resisting full gravity load as if it's merely a simply supported beam.
There are other restrictions likely as well. But, like I said, I've never used this in practice..... And, whatever you do, do NOT use this to resist seismic loads.
this connection called "Seated simple connection" see attached photo , but it is not commonly used .
I suggest you to use a simple shear connection either welded plat with column flange and bolted with the beam web or two angles back to back in place of single plate .
Thank you
 https://files.engineering.com/getfile.aspx?folder=d8943afe-ec74-416e-b77e-bab728d48da6&file=Seated_simple_connection.png
I think using angles as MC is usually not recommended. If you want to achieve a PR behaviour you can use a flush moment end plate.
Tristan861 -
I think it's and erection expediency issue. End plates can be more challenging for erection and the fabrication has to be a little more precise. Seated angle connections (with a shear plate) are much more forgiving.
Granted, I've never actually used them. But, I've talked to engineers that love them. None of them work in high seismic areas, I hope.
In that case, I would throw a stiffener to the tension cleat.