Hi:
I have a 36" water supply line that is used to fill a 12.5 million gallon remote
reservoir(about 6 miles from the pump). The fill line is a dedicated line, with
no tap offs along the way and several check valves in line.
Water leaving the plant is at 100 psi. Temperatures vary from 2C winter to
22C in the summer.
At the reservoir the 36" supply pipe splits into 2 smaller ones. One is 24" with a 24" flow control fill valve and the other line is a 14" pipe with a Neles type R
segmented ball valve.
The fill pressure at the reservoir dips down to 24psi during maximum fill of
14,000 gpm.
What has happned is that the smaller 14" flow control valve has cavitated and
perforated the valve body. It was suggested that we go to a Onyx Series Dac pinch valve.
My number crunching says that the 14" Neles valve presently used should fit the bill and that the Onyx pinch would be operating under tight conditions
with respect to delta p ceiling levels.
If the Neles seems to fit why did it cavitate out? Did I overlook something here?
Hi:
I have a 36" water supply line that is used to fill a 12.5 million gallon remote
reservoir(about 6 miles from the pump). The fill line is a dedicated line, with
no tap offs along the way and several check valves in line.
Water leaving the plant is at 100 psi. Temperatures vary from 2C winter to
22C in the summer.
At the reservoir the 36" supply pipe splits into 2 smaller ones. One is 24" with a 24" flow control fill valve and the other line is a 14" pipe with a Neles type R
segmented ball valve.
The fill pressure at the reservoir dips down to 24psi during maximum fill of
14,000 gpm.
What has happned is that the smaller 14" flow control valve has cavitated and
perforated the valve body. It was suggested that we go to a Onyx Series Dac pinch valve.
My number crunching says that the 14" Neles valve presently used should fit the bill and that the Onyx pinch would be operating under tight conditions
with respect to delta p ceiling levels.
If the Neles seems to fit why did it cavitate out? Did I overlook something here?