tumbleweed1
Electrical
- Sep 19, 2013
- 44
We've got a 4160V system with 4 generators FLA=370A (grounded Y) paralleled to a utility transformer. All gens and the util TX have 25A/10s NGRs on the neutral point. All NGRs have relays and monitors. All feeders with motors have zero sequence CTs, are ungrounded.
I understand neutral currents occur because of a few things:
- Ground faults with capacitive charging current discharge
- Variations of voltages between sources causing unbalanced currents to travel through the system
I've read a ton of published articles and threads on here regarding HR grounding. My questions are as follows:
I have calculated 3phase system charging current to be about 7A per generator (assuming 0.23uF/phase for generator capacitance, 0.5uF/phase surge caps, 136pF/ft*1000ft cable length), ~28A total for all generators.
1. To handle scenario 1 (4 gens max online) Is it wise to have each NGR sized to handle the total charging current from the whole system? Or would 25A be suitable as, ideally, the GF relay would trip accordingly?
2. Its my thought that the current through each NGR would be equal if they were sized equally and there was a fault on a feeder branch. How does one prevent tripping of an unfaulted feeder/generator from occurring?
3. In scenario 3, when only the utility is supplying the load feeders, is it sufficient to use Zero Sequence CTs to determine presence of fault currents to trip off necessary feeders? I guess the NGR on the TX will limit the current, correct?
4. Would a zigzag transformer connected to the main bus be useful for scenario 3 or for any other operation?
As you can tell, Im quite new to grounding schemes and would appreciate some input from those that understand this. Thanks!
I understand neutral currents occur because of a few things:
- Ground faults with capacitive charging current discharge
- Variations of voltages between sources causing unbalanced currents to travel through the system
I've read a ton of published articles and threads on here regarding HR grounding. My questions are as follows:
I have calculated 3phase system charging current to be about 7A per generator (assuming 0.23uF/phase for generator capacitance, 0.5uF/phase surge caps, 136pF/ft*1000ft cable length), ~28A total for all generators.
1. To handle scenario 1 (4 gens max online) Is it wise to have each NGR sized to handle the total charging current from the whole system? Or would 25A be suitable as, ideally, the GF relay would trip accordingly?
2. Its my thought that the current through each NGR would be equal if they were sized equally and there was a fault on a feeder branch. How does one prevent tripping of an unfaulted feeder/generator from occurring?
3. In scenario 3, when only the utility is supplying the load feeders, is it sufficient to use Zero Sequence CTs to determine presence of fault currents to trip off necessary feeders? I guess the NGR on the TX will limit the current, correct?
4. Would a zigzag transformer connected to the main bus be useful for scenario 3 or for any other operation?
As you can tell, Im quite new to grounding schemes and would appreciate some input from those that understand this. Thanks!