Parallel Backflow Preventers for Domestic Water

Status
Not open for further replies.

nuuvox000

Mechanical
Joined
Sep 17, 2019
Messages
344
Location
US
Hello, HVAC & Plumbing engineer here. Anyone know if it's worth doing two backflow preventers in parallel (RP type)? We always do the pressure reducing valves in parallel (one large, one small, typically) to avoid "chattering" of the valve at low flows. I've never seen someone design two backflow preventers but I'm wondering if that's useful for that type of valve as well. Thanks.
 
IMO, the purpose of the back flow preventer (BFP) is different from the pressure reducing valve. The BFP is to be closed and discharged through the relief valve once the flow direction is to be reversed, but won't be affected won't be affected because of the flow rate change.
 