A little background first:
We have been purchasing a centrifugal pump/motor combination for several years. We’ve frequently had problems in the field with the branch circuit fuses blowing during startup. They are Type J and sized at 175% of nameplate FLA. That being said, the motor is a 460Vmotor that has nameplate FLA of 2.9 and it runs about 3.1A while pumping hydraulic oil.
Anyway, I went out to get the locked rotor code from the motor nameplate on the power unit so I could calculate inrush for fuse sizing. It was blank as were a few other bits of typical information. I wrote the model and catalog numbers down and could not find them anywhere in the catalog. So, I called our Leeson dealer suspecting a custom motor. I was correct. The pump manufacturer is apparently taking a 3HP Jet Pump motor and de-rating it to 2HP on the nameplate so they can get a 50 deg. C rating versus 40 deg. C.
Has anyone ever heard of this before? I’m certainly going to bump the fuse size up a bit on future machines, but I’m afraid an inspector might have an issue at some point since they would not be aware of the “de-rating”. Nameplate FLA for this motor (as standard) is 3.8A.
Am I assuming correctly that a 3HP motor will have more inrush than a 2HP regardless of the size stamped on the nameplate? I’m wondering how much difference the 1HP would make for a 5A type J fuse.
We have been purchasing a centrifugal pump/motor combination for several years. We’ve frequently had problems in the field with the branch circuit fuses blowing during startup. They are Type J and sized at 175% of nameplate FLA. That being said, the motor is a 460Vmotor that has nameplate FLA of 2.9 and it runs about 3.1A while pumping hydraulic oil.
Anyway, I went out to get the locked rotor code from the motor nameplate on the power unit so I could calculate inrush for fuse sizing. It was blank as were a few other bits of typical information. I wrote the model and catalog numbers down and could not find them anywhere in the catalog. So, I called our Leeson dealer suspecting a custom motor. I was correct. The pump manufacturer is apparently taking a 3HP Jet Pump motor and de-rating it to 2HP on the nameplate so they can get a 50 deg. C rating versus 40 deg. C.
Has anyone ever heard of this before? I’m certainly going to bump the fuse size up a bit on future machines, but I’m afraid an inspector might have an issue at some point since they would not be aware of the “de-rating”. Nameplate FLA for this motor (as standard) is 3.8A.
Am I assuming correctly that a 3HP motor will have more inrush than a 2HP regardless of the size stamped on the nameplate? I’m wondering how much difference the 1HP would make for a 5A type J fuse.