Hi all, I am working on some designs for overhead conduit supports in a seismic region (SDC D). The contractor is proposing to use Unistrut frames to support the conduit. The anchorage they are proposing is Unistrut P2073A Post Bases and Hilti HDA-PR M10 undercut anchors.
My concern: Per the Unistrut catalog, the post bases come with 3/4" bolt holes. The diameter of the M10 undercut anchors is about 3/8". Therefore, the holes are even beyond "oversized" for the anchors per RCSC Table 3.1.
The post base anchorage is subject to sustained tension and shear during seismic events. Am I correct in my understanding that using this combination of anchors and hole size is not acceptable, even if we use a large enough washer?
Modelling the post base in Profis, the only HDA anchor size that will work with the edge distance/anchor spacing dimensions of the post base is the proposed M10. The Unistrut Ohio site states that the post base has 3/4" mounting holes for 5/8" anchors, but this is perplexing as it doesn't seem any of Hilti's offerings that I'm used to specifying would work with the bolt dimensions of the post base.
It seems like I need to push for either welding plate washers, or using custom post base plates? Would slip critical connections also be an option here?
Any thoughts are welcome, thanks in advance.
My concern: Per the Unistrut catalog, the post bases come with 3/4" bolt holes. The diameter of the M10 undercut anchors is about 3/8". Therefore, the holes are even beyond "oversized" for the anchors per RCSC Table 3.1.
The post base anchorage is subject to sustained tension and shear during seismic events. Am I correct in my understanding that using this combination of anchors and hole size is not acceptable, even if we use a large enough washer?
Modelling the post base in Profis, the only HDA anchor size that will work with the edge distance/anchor spacing dimensions of the post base is the proposed M10. The Unistrut Ohio site states that the post base has 3/4" mounting holes for 5/8" anchors, but this is perplexing as it doesn't seem any of Hilti's offerings that I'm used to specifying would work with the bolt dimensions of the post base.
It seems like I need to push for either welding plate washers, or using custom post base plates? Would slip critical connections also be an option here?
Any thoughts are welcome, thanks in advance.