CuriousElectron
Electrical
- Jun 24, 2017
- 192
Hi Guys,
Is the design decision to provide an overload protection for pad-mounted transformer based on expectation that the transformer would not be carrying more than its nameplate rating? If so, than the feeder and the secondary conductors don't need to be sized at 125% of their nameplate ampacity.
I know some pole mounted and pad mounted transformers can come with internal overloads, and if these units are selected, than does that mean that the cable needs to be upsized as well?
For example, I've got 100A on the secondary of the transformer. If I have already oversized the xfmr for the load that it will supply, I'd just size the wire based on this ampacity and provide a 100A breaker. I'd not need a 125 breaker with the larger size wire.
Am I correct on this?
Thanks,
EE
Is the design decision to provide an overload protection for pad-mounted transformer based on expectation that the transformer would not be carrying more than its nameplate rating? If so, than the feeder and the secondary conductors don't need to be sized at 125% of their nameplate ampacity.
I know some pole mounted and pad mounted transformers can come with internal overloads, and if these units are selected, than does that mean that the cable needs to be upsized as well?
For example, I've got 100A on the secondary of the transformer. If I have already oversized the xfmr for the load that it will supply, I'd just size the wire based on this ampacity and provide a 100A breaker. I'd not need a 125 breaker with the larger size wire.
Am I correct on this?
Thanks,
EE