Tillman
Chemical
- Dec 13, 2004
- 6
I have a 125 HP, 600 RPM, 480/60/3 225 FLA induction motor driving a piston compressor. It keeps tripping on O/L (set at 234A). I put a power analyzer to it, and this is what I got:
81 kW, 175 kVAR, 193 kVA, 0.42 PF, 3 phase A 231/231/231, 3 phase U 482/482/482.
Does this sound like a defective motor or there is something I can do to help with the PF?
Thanks,
81 kW, 175 kVAR, 193 kVA, 0.42 PF, 3 phase A 231/231/231, 3 phase U 482/482/482.
Does this sound like a defective motor or there is something I can do to help with the PF?
Thanks,