Outdoor Switchgear Clearance Question

Status
Not open for further replies.

deedo1124

Electrical
Dec 27, 2007
17
New landfill gas generating site with a unit substation (15kV-480V) installed on a containment pad. There is grating from the top inside of dike wall to equipment pad. Edge of pad extends 1'-6" from front and rear doors of 15kv gear. So as you approch the front and rear of the gear you are met with a 6" curb. Is this a violation of the NEC since there is not 3' of level working space at front and rear access doors?

Thanks for your input.
 
Replies continue below

Recommended for you

What NEC rule requires the work space to be level. Work space in front of 8.6 kV (Ø-grd) equipment is 4'.
 