OSHA Temporary Electrical Power

Status
Not open for further replies.

sjmgd997

Electrical
Aug 5, 2010
9
I had looked through OSHA to see if there were rules on the amount of distance from a load center to the equipment (such as a portable tool) it is supplying.

In essence, the temporary power I need is power for equipment like concrete vibrators and the like. The width of my building is about 170 feet.

One electrician I spoke with told me that the distance is 50 feet but I do not know if OSHA is the place where such distance limitations are found or not.

I looked in OSHA 1910 but could not find anything under the section on wiring methods.

 
Replies continue below

Recommended for you

See Article 590 in the National Electrical Code. If you can't find a specific reference there, the installation must meet the requirements for a permanent installation.



You sure don't want to run 170 feet of extension cord. You'll need a load center closer to the work, just to keep the voltage drop within reason. Or get a portable generator, if all you are using are concrete vibrators.

There are a lot of OSHA requirements regarding extension cords and inspectors will be looking since they cause a lot of accidents.

You can always ask OSHA if you have specific questions. Better to ask ahead of time.