Assume a net-metered facility that during a month, there are times when the facility is producing energy into the grid and times when the facility is consuming energy from the grid. This assumes the facility is large enough that the power factor (PF) is included in their billing calculation.

For such a case, do utilities calculate two PF's for a month (one for generation, one for consumption) or just one? If a single PF is calculated, how is it calculated?
 
Replies continue below

Recommended for you

The old school method would be to measure the incoming KVARHrs and KWHrs and the outgoing KVARHrs and KWHrs all on a monthly basis. PF would be calculated from those figures.
There would be two sets of ratchet equipped meters, one for incoming and one for outgoing.


Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Yes, go ask the utility. The metering system and penalties seem to be different for every one.
 