davidbeach
Electrical
- Mar 13, 2003
- 9,528
I'm looking for conductor properties for some late '30s or early '40s hollow copper conductors.
I have that the conductor is described as
350 kcmil Cu PH D 1319HSC2
I'm sure that at some point the 'kcmil' replaced an designation of MCM or it was 350,000 circular mils. All reports I have is that this is a hollow conductor.
I have the "Characteristics of Anaconda Hollow Copper Conductors (Anaconda Wire & Cable Company)" and "Characteristics of General Cable Type HH Hollow Copper Conductors (General Cable Corporation)" tables that are available in various sources and I can't match the supposed impedance of a line using this conductor.
For instance, there is a 17.30 mile line using this conductor, flat construction with 12 feet between conductors. The published impedance, in pu on 115kV and 100MVA bases, is
R1=0.02457
X1=0.10369
R0=0.06198
X0=0.35214
Using the Anaconda 378R1 design, and a triangle of equivalent spacing (how it would have been done by hand when the line was built), I get
R1=0.024187 98.44%
X1=0.101475 97.86%
R0=0.061579 99.35%
X0=0.349922 99.37%
When I calculate it using actual spacing, I get the same values for these parameters.
If I futz around with the parameters, I can get very close
R1=0.024567 99.99%
X1=0.103693 100%
R0=0.061958 99.96%
X0=0.35214 100%
But now I've got resistances and GMRs that don't match any of the conductor property tables I have.
Does anybody have other conductor property tables for any sort of hollow copper conductors besides the two I listed? Does anybody recognize the "PH D 1319HSC2" and have a way of converting that to a conductor specification that I might find on-line some where?
I have that the conductor is described as
350 kcmil Cu PH D 1319HSC2
I'm sure that at some point the 'kcmil' replaced an designation of MCM or it was 350,000 circular mils. All reports I have is that this is a hollow conductor.
I have the "Characteristics of Anaconda Hollow Copper Conductors (Anaconda Wire & Cable Company)" and "Characteristics of General Cable Type HH Hollow Copper Conductors (General Cable Corporation)" tables that are available in various sources and I can't match the supposed impedance of a line using this conductor.
For instance, there is a 17.30 mile line using this conductor, flat construction with 12 feet between conductors. The published impedance, in pu on 115kV and 100MVA bases, is
R1=0.02457
X1=0.10369
R0=0.06198
X0=0.35214
Using the Anaconda 378R1 design, and a triangle of equivalent spacing (how it would have been done by hand when the line was built), I get
R1=0.024187 98.44%
X1=0.101475 97.86%
R0=0.061579 99.35%
X0=0.349922 99.37%
When I calculate it using actual spacing, I get the same values for these parameters.
If I futz around with the parameters, I can get very close
R1=0.024567 99.99%
X1=0.103693 100%
R0=0.061958 99.96%
X0=0.35214 100%
But now I've got resistances and GMRs that don't match any of the conductor property tables I have.
Does anybody have other conductor property tables for any sort of hollow copper conductors besides the two I listed? Does anybody recognize the "PH D 1319HSC2" and have a way of converting that to a conductor specification that I might find on-line some where?