OC device in the neutral 3

Status
Not open for further replies.

stevenal

Electrical
Joined
Aug 20, 2001
Messages
3,869
Location
US
Seems like we've been getting more and more approval drawings from substation equipment vendors showing fuses in the neutral of the 120 V heating/lighting/receptacle circuits on these devices. We return marked up drawings with the neutral fuse removed. Is this just a case of international vendors being unfamiliar with USA single phase service? Or is this ever acceptable practice? Thanks.
 
A fuse in the neutral is never acceptable; you could blow the neutral fuse, interrupting the circuit but leaving energized conductors. You can use a 2-pole circuit breaker that interrupts both hot and neutral at the same time. Maybe they're confusing an ungrounded DC system with a grounded AC system.
 