Hi FacEngrPE
No, we are not contemplating forced cooling. The reason for that is that the peak capacity delivery is relatively only (140 MW), and the smaller conductor can provide a safety factor of 2 for the worst-case scenario.
The area is severally congested for the OH option, and the decision has to be made between an open trench with wetland vs. HDD. The cost of two HDDs will force us to use the open trench and be at the mercy of the permitting agencies.