Looking for a bit of help.
Our firm has a section of our machines subbed out to another company. They have a fairly old machine that PLC's battery died and they lost the software.
We've managed to source the software and I was supposed to re-load yesterday. I'm no PLC expert, still learning, have experience on GX developer and Mitsi PLC's.
The PLC is question was a Mitsi Q-series. The program given to us was on GX Works 2; which we have no experience of).
I re-loaded the software and got it to monitor. You could see inputs switching as buttons were pressed..
Looking at the software, the 'reset' button held for 5 sec would switch on a 'go home' marker. This was working as expected, but not all cylinders were going to home. When digging a bit deeper, there was no compressed air to the valves. There is a solendoid switch on the manifold which comes directly from an output of the PLC.
Going back to the panel, I followed solenoid cable back to output and noticed no outputs were illuminated. At this point, I checked the +24v on the cards, 24 was present. I then forced several outputs on in the plc, no output lights illuminated on the output cards.
Any suggestions to why we're not getting any outputs? I spent a good 4 hours going through the PLC parameters tabs, ensuring cards to rack set ups are correct etc etc
It's worth noting that this software was maybe not from GX Works2 originally, are there usually 'change over' issues? If yes, how could we get around it?
Any help appreciated.
Our firm has a section of our machines subbed out to another company. They have a fairly old machine that PLC's battery died and they lost the software.
We've managed to source the software and I was supposed to re-load yesterday. I'm no PLC expert, still learning, have experience on GX developer and Mitsi PLC's.
The PLC is question was a Mitsi Q-series. The program given to us was on GX Works 2; which we have no experience of).
I re-loaded the software and got it to monitor. You could see inputs switching as buttons were pressed..
Looking at the software, the 'reset' button held for 5 sec would switch on a 'go home' marker. This was working as expected, but not all cylinders were going to home. When digging a bit deeper, there was no compressed air to the valves. There is a solendoid switch on the manifold which comes directly from an output of the PLC.
Going back to the panel, I followed solenoid cable back to output and noticed no outputs were illuminated. At this point, I checked the +24v on the cards, 24 was present. I then forced several outputs on in the plc, no output lights illuminated on the output cards.
Any suggestions to why we're not getting any outputs? I spent a good 4 hours going through the PLC parameters tabs, ensuring cards to rack set ups are correct etc etc
It's worth noting that this software was maybe not from GX Works2 originally, are there usually 'change over' issues? If yes, how could we get around it?
Any help appreciated.