We have a freezer building with a design operating temperature of 0-degrees F. Because of this, we have a system with 50% Propylene Glycol, which should allow for anti-freeze safety in the building down to a temperature of -26. However, the Propylene Glycol increases the water density (Specific Gravity = 1.041) We also have a 500 gpm hose stream allowance per table 11.2.3.1.2. This hose allowance is approximately 50% of our total required flow rate, including sprinklers. My question is, should sprinkler calculations be done at the higher specific gravity, assuming that everything is happening at once, or can the assumption be made that by the time the fire department responds, and hose demand is needed, that the sprinkler system would be clear from the antifreeze? There is apparently enough pressure from the main to provide for the hose allowance and normal water flow, but the propylene glycol may cause a problem. I'm not the fire sprinkler designer - just trying to wrap my mind around this. Thanks