A cable (A) feeding an electric 3-ph motor using a softstart can be disconnected from a machine. Another cable (B) feeds control voltage to the same part of the machine. When this latter cable (B) is connected, it enables a control contactor feeding the 3 phase voltage to the softstart and the motor (it's not a start signal).
Upstream, I have overcurrent protection (3 fuses, 30A) for the motor.
So in panel: 30A Fuses - Contactor - Softstart
From panel to equipment: Cable (A) - Connector - Motor
Control Cable (B) - Connector - Junction box
A colleague wants to insert a breaker equipped with a special electronic trip unit between the fuses and contactor which is to trip when control cable (B) is disconnected. It would then be rearmed by push-button when the cable is connected.
I feel I am already protected by the contactor being disabled when (B) is disconnected, and disagree with him. NFPA79 art. 5.4.2 backs up my reasoning and to a lesser extent, cost.
He is concerned about voltage possibly being applied to the connector at the end of the disconnected cable (A). The connector is already fingersafe.
Any thoughts on this?
Upstream, I have overcurrent protection (3 fuses, 30A) for the motor.
So in panel: 30A Fuses - Contactor - Softstart
From panel to equipment: Cable (A) - Connector - Motor
Control Cable (B) - Connector - Junction box
A colleague wants to insert a breaker equipped with a special electronic trip unit between the fuses and contactor which is to trip when control cable (B) is disconnected. It would then be rearmed by push-button when the cable is connected.
I feel I am already protected by the contactor being disabled when (B) is disconnected, and disagree with him. NFPA79 art. 5.4.2 backs up my reasoning and to a lesser extent, cost.
He is concerned about voltage possibly being applied to the connector at the end of the disconnected cable (A). The connector is already fingersafe.
Any thoughts on this?