Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

NFPA 30 paragraph 16.5.2.2

Status
Not open for further replies.

ijour

Mechanical
Joined
Aug 1, 2014
Messages
2
Location
GR
in NFPA 30, paragraph 16.5.2.2, sub-paragraph 1) says "Automatic Sprinkler protection"
and
in NFPA 30, paragraph 16.5.2.4, sub-paragraph 1) says "Foam Water Sprinkler protection"

I think that all the NFPA 30 is talking about Foam extinguishing systems. Why is using the
"Automatic Sprinkler Protection"?

Thank you in advance for you answers.
 
Nfpa gives 2 options for fire fire protection, one with water only and one with foam/water. The foam is introduced at the sprinkler riser in either a 3 or6%. Mixed with the water and discharged via the sprinkler. This is considered a low expansion foam sprinkler system.

Do not forget to review FIGURE 16.8.1 Spill Containment and Liquid Spread Control for Protected Storage. This will let you know if you need foam based on the spill and or liquid spread control. This table is often missed and can result in a lot of $$$ if not taken into the design of the room/warehouse. For existing building retrofit with foam is the way to go.

 
Thank you very much.

Best regards
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top