Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

NFPA 2007 DENSITY/AREA CURVES 1

Status
Not open for further replies.

MaInspector

Civil/Environmental
Apr 2, 2009
19
Hello all,
I have a question about designing a full NFPA 13 Hydraulically calculated system using the density / area curves from figure 11.2.3.1.1 of the 2007 edition.
My question is when you have a large building (say 7,000 sq.ft.) with an Ordinary 2 occupancy classification, is it acceptable to design the system using the most remote 1,500 sq. ft. at .20 (gpm/ft2)Density or do you have to max out on the chart at 4,000 sq. ft. at .15 (gpm/ft2)Density?
 
Replies continue below

Recommended for you

You can use any point on the curve regardless of building size.

If you had a 50,000 sq. ft. building you could use the 1,500 sq. ft. point on the curve.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor