The committee has made a major shift regarding porches, balconies, decks, and ground floor patios serving dwelling units in buildings of Type V construction. Type V construction applies to the entire building, and not just the construction of the balcony. This rule applies to the exterior or “open” spaces accessible only from the dwelling unit itself, and not a corridor or breezeway that is shared among multiple dwelling units. During one of the model building code development process hearings, there was a major debate about allowing a Type V construction multifamily residential building protected with an NFPA 13R system to qualify for a one story height increase. Many of the building code proponents are extremely concerned about property protection. There is a history of fires starting on exterior open porches that have traveled up through each unprotected balcony and that eventually breached the attic, causing a total loss of the building. The main causes of these fires have generally been discarded cigarettes or unattended or improperly extinguished cooking grills. The fire codes do not allow grilling on porches, but this can be difficult to enforce. The fatality rates from these incidents are very low and are within the parameters of the scope and purpose of NFPA 13R. However, the committees that develop the model building codes agreed that, in order to recognize the height increase for an NFPA 13R system, these porches would be required to be sprinkler protected.
The NFPA 13R committee has resisted requiring sprinklers on these porches for several cycles, citing various concerns. The concerns range from the need for freeze protection to the question of the effectiveness of dry sidewall sprinklers installed under obstructed construction, considering exterior factors such as how wind might affect the spray pattern or response times. However, for the 2013 edition, the committee acquiesced to correlate with the model building code. Many sprinkler contractors and fire officials are unaware of the requirements found in the building code in regards to these porches, decks, patios, and balconies, often only finding out the details of the requirement from a building official around the time they attempt to get a certificate of occupancy. So, this correlation with the building code helps make sprinkler contractors aware of the requirements on these open areas before they begin working.
This section also is explicit in that if there is not a roof or deck above the balcony or porch, no protection is required; a balcony under an eave with a soffit or fascia board would not be mandated to have sprinklers added.