Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

nfpa 13 suspended continuous lighting track obstruction

Status
Not open for further replies.

dxbhd

Specifier/Regulator
Joined
May 1, 2014
Messages
2
Location
AU
Hi all,
I have a problem with a few 20 metre long suspended lighting tracks possibly baffling the sprinklers in a retail shop. The light assembly is 109mm high x 270mm wide and is suspended by thin wires. The bottom of the lighting is 380mm below the sprinkler deflectors. Would this be ok? I don't have a copy of the code just now, however will purchase one soon. What clauses would this come under. From some years ago I vaguely remember nfpa had quite good info on esfr suspended obstructions but was lacking a bit on standard spray sprinkler obstructions in that it assumed the obstruction was a solid vertical to the ceiling.
Thanks in advance for any advice
 
So are you using esfr heads in this installation or a different head ??

Still translating the measurements
 
they have standard spray sprinklers.
 
you are closer than 457mm to a sprinkler head.

from nfpa 13 2013 edition


8.5.5.2* Obstructions to Sprinkler Discharge Pattern Development.

8.5.5.2.1 Continuous or noncontinuous obstructions less than or equal to 18 in. (457 mm) below the sprinkler deflector that prevent the pattern from fully developing shall comply with 8.5.5.2.



3.3.18 Obstruction.

3.3.18.1 Continuous Obstruction. An obstruction located at or below the level of sprinkler deflectors that affect the discharge pattern of two or more adjacent sprinklers.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top