I've created this cartoon to try to solve an issue with a 10k +/- load coming from a new 5-1/2" sqr header post (I didn't provide the post, just evaluating the wall). Post supports a new bearing wall in a 3 story cottage. Post lands on an existing 8" block (empty, no grout) exterior wall. The new addition turns this exterior wall into an interior wall though with new framing landing on the wall 16" oc. Running the numbers with 2011 masonry code assuming f'm=1000 psi, bearing in the block doesn't work. Sandy soil, so I'm going with 2000 psf for soil bearing.
So attached is my first past. I don't have much experience in residential remodel, mainly focus is heavy industry. But I'm interested in this type of work, and more importantly, you're input. So please go easy and keep the condescension to a minimum
I'm sure there are several ways to skin this, but I'm looking for a practical and workable solution. My main concerns are the best way to lag the existing wall to the new concrete. Are there better ways then doweling with rebar?