Good Morning,
I have a project where an existing reinforced concrete transformer pad (20'-6"L x 13'-0"W x 2'-6"Th) has some significant spalling damage from an equipment fire on top. The spalling/pitting is 3" in some areas on top. This was a hot fire that went for hours. My question is instead of trying to sandblast and patch the damaged areas with some cementitious/polymer product, can a full concrete overlay be installed over the pad? Possibly a 4" overlay with WWF for reinforcement?
My thoughts on both approaches:
Patch Option:
-May not bond well to the existing pad which could lead to deterioration in the future
-Outdoor exposure to the elements may cause the patch to deteriorate
-may require more time to sandblast and chip away damaged material to reach good concrete. (Schedule is important) Also, don't want to damage rebar in the process.
-May require forensic analysis by a third party engineer to select appropriate product. (Schedule)
4" concrete overlay Option:
-Will the overlay bear the heavy load (total 325k) from the transformer or will it crush/be pulverized on top of the existing pad? (This is my question) If the overlay has a solid bearing surface (top of pad) then will it not support the load?
-Must check if new transformer can be set higher. Check connections.
-Must check additional dead load from add'l material, although I suspect that this won't cause the pad to settle.
-Must sandblast and chip away damaged material anyway.
-Confidence in contractor to form and pour the overlay is higher than finding a specialty contractor familiar with patching. (Schedule)
Overall I believe the mass concrete pad is still fine to support the heavy transformer (325k). Lastly, this is a static load not a dynamic vibrating load.
Any feedback or comments would be great! Thank you!
I have a project where an existing reinforced concrete transformer pad (20'-6"L x 13'-0"W x 2'-6"Th) has some significant spalling damage from an equipment fire on top. The spalling/pitting is 3" in some areas on top. This was a hot fire that went for hours. My question is instead of trying to sandblast and patch the damaged areas with some cementitious/polymer product, can a full concrete overlay be installed over the pad? Possibly a 4" overlay with WWF for reinforcement?
My thoughts on both approaches:
Patch Option:
-May not bond well to the existing pad which could lead to deterioration in the future
-Outdoor exposure to the elements may cause the patch to deteriorate
-may require more time to sandblast and chip away damaged material to reach good concrete. (Schedule is important) Also, don't want to damage rebar in the process.
-May require forensic analysis by a third party engineer to select appropriate product. (Schedule)
4" concrete overlay Option:
-Will the overlay bear the heavy load (total 325k) from the transformer or will it crush/be pulverized on top of the existing pad? (This is my question) If the overlay has a solid bearing surface (top of pad) then will it not support the load?
-Must check if new transformer can be set higher. Check connections.
-Must check additional dead load from add'l material, although I suspect that this won't cause the pad to settle.
-Must sandblast and chip away damaged material anyway.
-Confidence in contractor to form and pour the overlay is higher than finding a specialty contractor familiar with patching. (Schedule)
Overall I believe the mass concrete pad is still fine to support the heavy transformer (325k). Lastly, this is a static load not a dynamic vibrating load.
Any feedback or comments would be great! Thank you!