neutral grounding reactance manufacturer

Status
Not open for further replies.

JLuc

Electrical
Mar 30, 2007
62
Hi all,

I'm looking for a neutral grounding reactance to install on a 25 kV Y transformer.

This is to reduce de phase-ground fault current. The reactance has to be 35 ohms.

I would like to know manufacturers or distributors of this kind of product, in Canada, that could help us with the specifications and also supply the product.

Thanks
 
Replies continue below

Recommended for you

Reactance or resistance? Grounding reactors are very rare these days, at least in North America.
 
I'm talking about reactance.

We need it to install on the high side of a step up transformer (600/25000Y), for a 2MW hydro plant.

The goal is to reduce the phase-ground fault current and to stay solidly grounded at the same time. Utility requires that.

I will communicate with Trench, as the seem to be a good supplier of air core reactors.

 
Yes, Trench is one the usual suspects for reactors.
 