I've recently been looking at a solar design which has an inverter interface to the utility system with the AC output of the inverter utilizing a Delta-Delta steup up transformer to output the inverter voltage at 480V. The instruction manual mentions that for a 4-wire utility system a neutral can be connected inside the inverter (4th wire) however it would only be used for neutral sensing. The inverter ties into the utility through a reverse fed feeder breaker in an upstream panel.
Obviouly with a delta connected transformer there is no neutral current flow but I'm curious if there were loads connected in the panel that had a neutral or were connected L-G would this mean that all neutral current would have to return to the utility source and none would return to the inverter? Is there an issue with this if all unbalanced current returns to utiliy although some of the supply is coming from the inverter?
Also how does this effect ground fault detection and clearing on the AC system. Does this mean that all ground fault current would have to flow to utility source and none would flow back to inverter? Again is there an issues with this as questioned above?
Thanks for all the help.
Obviouly with a delta connected transformer there is no neutral current flow but I'm curious if there were loads connected in the panel that had a neutral or were connected L-G would this mean that all neutral current would have to return to the utility source and none would return to the inverter? Is there an issue with this if all unbalanced current returns to utiliy although some of the supply is coming from the inverter?
Also how does this effect ground fault detection and clearing on the AC system. Does this mean that all ground fault current would have to flow to utility source and none would flow back to inverter? Again is there an issues with this as questioned above?
Thanks for all the help.