prc
Electrical
- Aug 18, 2001
- 2,019
A 100 MVA 11/132 KV generator transformer with OLTC is connected to grid.At rated tap( 138 kV, there is no neutral current.
The grid voltage was 133 kv and transformer terminal voltage after regulation is also near to it.Line currents are also equal and balanced.
When tap is changed to 133 KV, grid voltage was 135 KV and after regulation the voltage difference between transformer terminal voltage and grid was 5-6 Kv and a neutral current of 23 A ( nearly 5% of full load current) is seen.When line currents which are not balanced,are vectorially added, the net current is coming near to 23 A.Customer says transformer is faulty and that is why neutral current is coming!
Waht exactly is happening when we a trf with terminal voltage say 129 Kv is connected to infinite grid at 135 KV?Will neutral current will be generated on that occasion? If terminal voltage is more than grid voltage what will happen?Then also neutral current is seen.
The grid voltage was 133 kv and transformer terminal voltage after regulation is also near to it.Line currents are also equal and balanced.
When tap is changed to 133 KV, grid voltage was 135 KV and after regulation the voltage difference between transformer terminal voltage and grid was 5-6 Kv and a neutral current of 23 A ( nearly 5% of full load current) is seen.When line currents which are not balanced,are vectorially added, the net current is coming near to 23 A.Customer says transformer is faulty and that is why neutral current is coming!
Waht exactly is happening when we a trf with terminal voltage say 129 Kv is connected to infinite grid at 135 KV?Will neutral current will be generated on that occasion? If terminal voltage is more than grid voltage what will happen?Then also neutral current is seen.