I do not have my old "H" joist catalog with me. I need the listed maximum load capacities for the following "H" series joists:

22H6 30' span
22H9 40' span
24H10 45' span
14H3 17' span

Thanks in advance!
 
Replies continue below

Recommended for you

jike,

From 1974 - TL/LL (LL based on L/360)

22H6 - 30' span - 313/228 flexure controlling
22H9 - 40' span - 323/161 flexure controlling
24H10 - 45' span - 315/152 flexure controlling
14H3 - 17' span - 376/305 shear controlling

 
22H6 30' span - 313 plf TL, 228 plf LL (L/360)
22H9 40' span - 323 plf TL, 161 plf LL (L/360)
24H10 45' span - 315 plf TL, 152 plf LL (L/360)
14H3 17' span - 376 plf TL, 305 plf LL (L/360)
 
Thanks! That is exactly what I needed! Regards!
 