Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations LittleInch on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Need help with sizing a filter in metric 1

Status
Not open for further replies.

Airforce2

Mechanical
Joined
Dec 30, 2004
Messages
67
Location
AU
Hi everyone,

I feel silly for asking this, but this is a metric situation.

I have been requested by a client to size a filter for a roof top unit.

The unit is rated at delivering 1500 l/s and the client wants 1.7 m/s
velocity across the filter.

Would someone be able to assist me with the formula to work out the filter sizing? I came up with an area of .88, but am lost on how to convert that to an actual size in ?mm x ?mm.

I need to get used to the metric system once again.

I appreciate any assistance you can give me.

THANKS
 
0.88 Sqm is right. You can arrive at 0.88 Sqm by using a filter of size 0.94m x 0.94m or 1m x 0.88m or 2m x 0.44m - I can go on and on.

However, the filter dimensions would depend on the coil dimensions. The manufacturer would be able to give you the size of the filter or you can physcially check the dimension of the filter from the unit itself.

Trust this helps

HVAC68
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top