Need for Load Control Module when paralleling generator with utility?

Status
Not open for further replies.

oufis

Electrical
Joined
Nov 21, 2011
Messages
1
Location
CA
Hi,
On a project that I am working on, the client is requesting to be able to test the generator when it is paralleled with the utility (testing up to 80-100% of the output power).
Do I really need to have a Load Control Module to be able to test the generator up to 80-100% of the output power?

Thanks
 
How else would you get it to a specific loading?
 
If you are able to use a droop speed setting you set the speed slightly overspeed and let the droop take care of it.
With 3% droop, a no load setting of 61.8Hz will give 100% loading at 60 Hz.
Oce you are synchronized, raise your speed setting and the speed won't change but the unit will pick up the load.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Be sure to check with the local utility to see what they require for a distributed generation interconnection. Any closed transition might require a full interconnection package including an impact study, transfer trip to the utility substation breaker and a specific choice of transformer configuration.
 