Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Need 4-20mA converted to fiber optics

Status
Not open for further replies.

dubbed

Mechanical
Jul 17, 2006
37
I have a 4-20mA pressure transducer in a well and the cable is run several hundred feet in the ground.

We have had problems with lightening and are looking to covert the signal to fiber to isolate it from our DDC.
anyone know a converter that does this?

We also need power isolators which I don't know much about.

Thanks
 
Replies continue below

Recommended for you

have a look at
Have you considered putting a galvanic isolator and / or surge arrestor at the surface?


----------------------------------
image.php

If we learn from our mistakes I'm getting a great education!
 
thanks!

will also look into a galvanic isolator and / or surge arrestor
 
The purpose of the powered Isolator would be more than likely due to the distance from the source to the reciever while also providing isolation of the two areas. If you take into account voltage drop for the wire a powered isolator will help but may be required to be repeated based on the distance traveled. The isolator can provide an intrinically safe signal from a single or dual channel isolator repeated from the hazardous location to the safe location such as the model 9160's from Stahl. can also provide information on the products that can help with this application.

RL
 
ScottyUK's solution is the best in my humble opinion provided you have power available at both ends. FO cable is immune to lightning unless it gets a direct hit of course.
Roy
 
Weed Instruments.. I took them out of the dark ages with a new micro design for their flagship product.


dubbed: Is there a question here? A specific question?
I see the sketch what is your specific question?

Keith Cress
kcress -
 
I don't understand the purpose of the relay, or the 2nd battery for that matter.
Your transmitter only draws 20 mA so a battery will last a long time.
You will also need to supply the FO converter.
Perhaps just one battery with a small solar panel.
Another option with a well that only changes slowly is to just sample the level for a few seconds every hour that way you could run on a couple of small dry batteries without a charger.
Roy
 
Status