We are using #4/0 AWG dual rated "type-W/RHH" flexible power cable on a job. The manufacturer's data sheet lists the cable as rated 405A @ 90C based on NEC table 400.5. We will be terminating the cable to a power terminal block rated 75C. The cable is going to be installed in an uncovered cable tray in a single row, no spacing between cables. No temperature deration is required - it's a temporary 3-week job and it is cold outside.
Based on the RHH rating:
The conductor is rated 405A per table 310.17 90C column. Must be multiplied by 0.65 per article 392.11. New rating is 263.25A @ 90C. Per article 110.14(C), the cable ampacity must not exceed 230A per table 310.16 based on 75C column. The lower of the two values is 230A, so that must be my cable ampacity. Correct?
Based on the type-W rating:
If I had the cables in "free air" run on the ground and spaced appropriately, the ampacity of the cables @ 90C would be 405A. If I were using camlock connectors on both ends (rated 405A @ 90C), the entire cable could be rated 405A, right? If I take that same cable and terminate to that terminal block or to a breaker, would I then have to use 230A ampacity per article 110.14(C)?
Another question:
What is the purpose of article 392.11(B)(3) if article 110.14(C) forces you to limit the ampacity of the 75C column of 310.16?
Based on the RHH rating:
The conductor is rated 405A per table 310.17 90C column. Must be multiplied by 0.65 per article 392.11. New rating is 263.25A @ 90C. Per article 110.14(C), the cable ampacity must not exceed 230A per table 310.16 based on 75C column. The lower of the two values is 230A, so that must be my cable ampacity. Correct?
Based on the type-W rating:
If I had the cables in "free air" run on the ground and spaced appropriately, the ampacity of the cables @ 90C would be 405A. If I were using camlock connectors on both ends (rated 405A @ 90C), the entire cable could be rated 405A, right? If I take that same cable and terminate to that terminal block or to a breaker, would I then have to use 230A ampacity per article 110.14(C)?
Another question:
What is the purpose of article 392.11(B)(3) if article 110.14(C) forces you to limit the ampacity of the 75C column of 310.16?