I'm curious if the following hypothetical installation would violate article 225.30 of the NEC.:
1000kVA 480V transformer outside of building feeds two 600A MCCs inside of building. Each MCC has a main breaker.
Since the total load is less than 2000A I don't think it meets the requirements of 225.30(C) apply. This is a question mostly about terminology - I'm not sure if there are multiple feeders to the building because (1) the MCCs are feed from the same source, (2) only one feeder (it's not a service) supplies power to the transformer, (3) the transformer supplies power only to the MCCs in the building, and (4) the only power into the building is from that transformer.
I see two potential arguments that could be made:
(1) there are two feeders to the building because there are two seperate MCCs
(2) there is only one feeder that 'supplies power to the building' which is the transformer feeder because of the points listed above
Please let me know your opinion
1000kVA 480V transformer outside of building feeds two 600A MCCs inside of building. Each MCC has a main breaker.
Since the total load is less than 2000A I don't think it meets the requirements of 225.30(C) apply. This is a question mostly about terminology - I'm not sure if there are multiple feeders to the building because (1) the MCCs are feed from the same source, (2) only one feeder (it's not a service) supplies power to the transformer, (3) the transformer supplies power only to the MCCs in the building, and (4) the only power into the building is from that transformer.
I see two potential arguments that could be made:
(1) there are two feeders to the building because there are two seperate MCCs
(2) there is only one feeder that 'supplies power to the building' which is the transformer feeder because of the points listed above
Please let me know your opinion