Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

NDE in lieu of hydrostatic testing for boiler external piping

Status
Not open for further replies.

Trebormech

Mechanical
Jun 13, 2016
14
Is there ever a case where sufficient NDE of boiler external piping can be done in lieu of a hydrostatic test?

Case in point: Installing a new steam header in a multiple boiler facility where isolation for hydrostatic test would be difficult, if not impossible, due to the number of isolation points involved.

I believe the administrative jurisdiction and technical responsibility for the piping in this case would be ASME B31.1, instead of BPVC section I, because it is a multiple installation common header, according to Fig. PG-58.3.1(a) "Code Jurisdictional Limits for Piping - Drum Type Boilers"

Thank you.
 
Replies continue below

Recommended for you

If these are new boilers being installed then the piping must be hydrostatic tested in accordance with PG-99 of ASME Section I.

If you are replacing existing steam header then NDE may be acceptable in lieu of pressure test as described in the NBIC Part 3. You would need concurrence of the Authorized Inspector and Jurisdiction, if required.
 
I concurr with bvp66. If this is for an existing installation and you are replacing with a new steam header, the NBIC would be used with NDT in lieu of a hydrostatic test.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor