- Jan 14, 2013
- 60
Greeting eng-tips forums,
I am working on designing a 18m cantilever pole light tower according the the National Building Code of Canada, using Commentary I and the dynamic procedures.
The details are as follows:
Wind pressure, q: 0.28 kPa
Height, H: 18.25 m
Width ave, w: 0.4 m
Natural Freq, fn: 0.045 Hz (EI~ 67*10^12 Nmm2, p~ 105 kg/m)
Critical Damping, B: 0.5%
Working through paragraphs 46 to 56 of Commentary I, I have come up with a Cg (gust factor) of 9.4. This value struck me as being very high, is anyone familiar with this piece of code and willing to chip in two cents?
Also, if you are familiar with the code, is figure I-24 of the Commentaries intended for this type of design and can you point out any recommended reading to understand their use of Cf and Cp separably?
Regards,
wadavis