RIMJ
Mechanical
- Jun 25, 2002
- 3
The engine is a one year old Wisconsin V465D natural gas fuelled unit [the derated hp for natural gas at 1000 feet above sea level at 1800 rpm is about 35 hp]. This engine ran without difficulty for about a year. Recently, however it has exhibited the following problem.
The driven load, a centrifugal pump has a brake hp of about 25 hp [when we can get the engine up to speed].
The engine will not start without the shutoff valve on the gas supply line being pinched almost closed. This did not use to be the case. Once the unit is idling, it can be brought up to speed by opening the shutoff valve very slowly. A tee has been installed right at the inlet to the carburettor, and a pressure gauge read while the unit is running displays rapid pulsations.
We suspect an issue with the regulator, but can an expert in the field be more specific in the diagnosis?
Thanks in advance for any ideas.
(The engine is fed by a fuel gas line with a regulator [brand/model not known, but it is a self operated type]. Orifice size is reported to be 3/16 inches. The piping to the engine consists of a gas meter and fuel lockoff valve, then 10 feet or less of 1 inch pipe which passes through the wall of the building, a shutoff valve inside the enclosure, then about 5 feet of 1/2 inch line and flex hose reducing to 1/4 inch at the engine. The engine is designed for an inlet gas pressure of 4 - 6 inches water column and using 1050 BTU gas requires about 25 x 12 = 300 cubic feet of fuel per hour.)
The driven load, a centrifugal pump has a brake hp of about 25 hp [when we can get the engine up to speed].
The engine will not start without the shutoff valve on the gas supply line being pinched almost closed. This did not use to be the case. Once the unit is idling, it can be brought up to speed by opening the shutoff valve very slowly. A tee has been installed right at the inlet to the carburettor, and a pressure gauge read while the unit is running displays rapid pulsations.
We suspect an issue with the regulator, but can an expert in the field be more specific in the diagnosis?
Thanks in advance for any ideas.
(The engine is fed by a fuel gas line with a regulator [brand/model not known, but it is a self operated type]. Orifice size is reported to be 3/16 inches. The piping to the engine consists of a gas meter and fuel lockoff valve, then 10 feet or less of 1 inch pipe which passes through the wall of the building, a shutoff valve inside the enclosure, then about 5 feet of 1/2 inch line and flex hose reducing to 1/4 inch at the engine. The engine is designed for an inlet gas pressure of 4 - 6 inches water column and using 1050 BTU gas requires about 25 x 12 = 300 cubic feet of fuel per hour.)