Natural gas pipe selection

Status
Not open for further replies.

dallas

Electrical
Joined
Oct 21, 2002
Messages
6
Location
US
Could someone please tell me if this is correct:

Appliance BTUh = 72000
Natural gas BTU/CF= 1025

72000/1025= 70.2 CF/hr

at 8 psi inlet pressure

Pipe size of 1 inch is fine correct.
 
Dallas:

You need to factor in the length of run of your pipe and all the fitting (elbows, tees, valving, etc) to see if the resultant P-drop results in satisfactory supply pressure to whatever it is you are delivering the gas. Many appliances "expecct" a minimum supply gas pressure.

Consult the IFGC (International Fuel Gas Code) for quick and easy line size selections.
 
Hello

Flow of high pressure gas in standard wall pipe is usually accompanied by a considerable pressure drop and decrease of the density along the entire line. The flow is expressed by the equation: Q = d to the 8/3 power x the sq root of (P1 squared minus P2 squared), all divided by the square root of (Sa x L), then multiply the product of the division x 33.95

Q = Flow of free gas at 60 degrees F (cubic feet/min.)
d = Inside dia. of the pipe in inches
P1 = Initial pressure (psi absolute)
P2 = Final pressure (psi absolute)
Sa = Specific gravity of the gas (air = 1)
L = Effective length of the pipeline in feet

 