Probably. The transformer needs to be accessible and you must provide transformer protection and 120V circuit protection in accordance with the NEC. This will require additional circuit breakers or fuses on the secondary side of the step-down transformer. You can't really rely on the 277V breaker back in the panelboard to protect anything downstream of the transformer.