MV Power plant

Status
Not open for further replies.

Coca1995

Electrical
May 16, 2023
11
Hey guys,

Newbie eng here. Working on a powerplant design where we have 4 x2.5 MW, 4.16 kV generator and one backup generator which only operates when one of the 4 generator is down to achieve N-1 redundancy. Issue is i cant decide on which bus system to be used. Using a common bus seems more favourable. My question being do i need to worry about frequent bus faults in 10 MW natural gas system? Whats your opinion?
 
Replies continue below

Recommended for you

Normally one would split the bus with any redundant loads divided between the busses. If the emergency generator is not capable of running the entire plant then a third bus is applied wich supports critical loads only. This simplifies load shedding. The busses are interconnected by tie breakers and run as a common bus under normal operation.
 
This would be to many devices for a ring bus, but a breaker and a half is possible. The down side is it requires 50% more breakers. Best arrangement is source/load on each rung.
 