Dear Mr. NickParker (Electrical)
" ...the control power to the starter is tapped from the line side of the circuit breaker. Interlock is made such that control power is unavailable when the breaker is off/trip....It seems that when the breaker trips, the contactor also trips. Is it desirable in the event of short circuit? ...."
1. In the IEC world (IEC 60947-4-1), [a motor starter] is typically made up of i) a switching device (contactor) and ii) an overload protection device (OL). These i) and ii) MUST be coordinated with iii) a short-circuit protection device (SCPD)[e.g. MCB, MCCB or fuse]; a device capable of providing protection to i) and ii) being damaged by high short-circuit current. That is, the contactors and overloads are NOT designed to withstand the (short-circuit current) [which can be 20-50kA].
2. Complete coordination tables (acc. IEC 60947-4-1)are available from the manufacturers for i), ii) and iii) according to the rated operation voltage, motor power and the rated short-circuit current; classed into [Type 1 or Type 2] coordination.
3. a) Type 1: in short-circuit condition, the contactor or starter does not endanger persons nor installations and will not be able to then operate without being repaired or having parts replaced,
b) Type 2: in short-circuit condition, the contactor or starter does not endanger persons nor installations and will be able to operate afterwards. The risk of contacts light welding is acceptable.
Che Kuan Yau (Singapore)