Motor Seq Currents Use

Status
Not open for further replies.

IndianTechEngg1001

Electrical
Mar 22, 2010
81
I was going through ETAP Help Files which states,

X0

Zero sequence reactance in percent (machine base); used for calculating short-circuit currents for unbalanced faults.

X2

Negative sequence reactance in percent (machine base); used for harmonic analysis.

Is it right?
 
Replies continue below

Recommended for you

X2 is needed for unbalanced faults. X0 is needed for unbalanced faults with a connection to earth. See some book in power system analysis.
 