Motor lead splices

Status
Not open for further replies.

podo

Electrical
Jun 1, 2004
7
I know that we have all tape-spliced motor leads in motor junction boxes, but I have never seen any written procedures for this process, i.e. what type of tape(s) to use, how many layers, etc. These would be 50 - 200 HP AC motors, 1000 volt or 4000 volt. The terminal boxes are rather small and the splices would have to be taped. There is no room for the pre-formed splice boots. Any help would be appreciated.
Thanks,
Podo
 
Replies continue below

Recommended for you

My personal preferance is to use high press type lugs, bolted together with S/S bolts. One layer of good quality PVC tape to allow easy removal, 3 or 4 layers of linerless 44KV splicing tape. More layers the higher the voltage. Then cover with good quality cold weather electrical tape.
 
Use of non-commodity-grade unshielded MV cable may be considered for controller-to-motor cabling to limit the increased volume generally required for shielded-cable installation.

I second AFab’s callout of seamless-copper-tubing tool-compressed lugs for compact and reliable connections. Silicon-bronze hex-machine bolts with phosphor-bronze internal-star lockwaxhers are have a good track record.

Various splitbolts or aluminum setscrew lugs with assorted junkbin hardware get used when nobody’s looking, until their failure blows holes in motor j-boxes. For ANSI regions, tight quarters may be somewhat relieved with application of NEC 430-12 terminal-box sizing.

Suggested is the tried-and-true non-adhesive-backed varnished-cambric / linerless-rubber or silicone / 10-mil vinyl-tape finish. (Cambric permits convenient “clamshell” stripping during teardown.) in MV splicing, this method is sometimes refferred to as a built-up/field-fabricated
(compared to kit) application.

Tape “insulation equivalent…” thickness implied by NEC 110-14 seems a bit vague and of marginal guidance. Kerite has drawings of MV-unshielded splices, for they are a long-time major proponent of unshielded 5kV-class [NOT unishileded] materials. Kerite prints are available through
EPR/CSPE (or CPE) insulation/jacket flexibility {stranding aside} is typically more desirable versus XLPE/PVC versions. The increased material cost is typically offset by reduced installation effort and increased long-term durability. 1kV circuits may be specified with 2kV unshielded EPR RHW-2 cable. 4kV circuits may be specified with 5kV unshielded EPR/CSPE MV90 or MV105 cable.

Minnesota Mining and Plymouth Rubber are two popular brands of insulating materials.
 
3m makes high voltage splice kits for high voltage stress cones terminations, check with them.
 