Suggestion: Visit Reference
1. ANSI/NEMA Standards Publication/No. MG 1-1978 (or subsequent ones) "Motors and Generators"
a) Reference 1 Paragraph MG 1-1.43 "Service
Factor-Alternating-Current Motors" defines the Service Factor as follows
"The service factor of an alternating-current motor is a multiplier which,
when applied to rated horsepower, indicates a permissible horsepower
loading which may be carried under the conditions specified for the
service factor (see MG 1-14.35). So, it is a good idea to look at it further.
b) Reference 1 Paragraph MG 1-14.35 "Application of
Alternating-current Motors with Service Factors" that states:
b.A) General. A general-purpose alternating current motor or any
alternating-current motor having a service factor in accordance with MG
1-12.47 is suitable for continuous operation at rated load under the
usual service conditions given in MG 1-14.02. When the voltage and
frequency are maintained at the values specified on the nameplate, the
motor may be overloaded up to the horsepower obtained by multiplying
the rated horsepower by the service factor shown on the nameplate.
When the motor is operated at any service factor greater than 1, it may
have efficiency, power factor and speed different from those at rated
load, but the locked-rotor torque and current and breakdown torque will
remain unchanged.
b.B) Temperature Rise - Integral Horsepower Alternating-Current
Motors. When operated at the service factor load, the motor will have a
temperature rise as specified in MG 1-12.42.1.b.
b.C) Temperature Rise - Fractional Horsepower Alternating-Current
Motors. When operated at the service factor load, the motor will have a
temperature rise as specified in MG 1-12.41, par. A.
That what the "Bible" says. Therefore, one must watch nameplate
motor rated voltage and motor rated frequency shown on the motor
nameplate when the service factor is used. This is a big risk since
everyone knows what those motors are getting at their terminals.
Therefore, simply, risks are fairly high, if the motor does not have a
rated frequency and rated voltage stabilizers (which can get expensive!)
while running within the service factor horsepower range.