bookowski
Structural
- Aug 29, 2010
- 983
When using slab on composite deck is it typical to ignore moment connections when designing floor beams for gravity loads? I guess there are two parts - is this acceptable for the beam design and is this acceptable for the connection design.
If considering the moment connection then the composite action would be lost in negative moment regions but you get the benefit of the end restraint. If you consider it simply supported you get composite behavior but neglect the contribution of the end restraint.
From what I see so far it seems like people design for gravity as a simply supported beam and then design for lateral with moment connections.... does that make sense? I've seen discussions on this topic on here before but never had to deal with it (I believe that blodgett is referenced for this discussion). It also seems like people always refer to these moment connections as 'wind' connections... when would you have wind but not have to satisfy seismic also? Is this considered valid for seismic?
thanks
If considering the moment connection then the composite action would be lost in negative moment regions but you get the benefit of the end restraint. If you consider it simply supported you get composite behavior but neglect the contribution of the end restraint.
From what I see so far it seems like people design for gravity as a simply supported beam and then design for lateral with moment connections.... does that make sense? I've seen discussions on this topic on here before but never had to deal with it (I believe that blodgett is referenced for this discussion). It also seems like people always refer to these moment connections as 'wind' connections... when would you have wind but not have to satisfy seismic also? Is this considered valid for seismic?
thanks